Unexpected KNX TP1 Control Field: Frame starts with 0xBE instead of expected 0xBC #496
Replies: 5 comments 2 replies
-
|
Hi, |
Beta Was this translation helpful? Give feedback.
-
|
Where are those “raw bytes” coming from (TP-UART/NCN5120, USB interface, KNXnet/IP tunneling/router, etc.) ? |
Beta Was this translation helpful? Give feedback.
-
|
In TP1, section 2.2.2 Control field of the KNX docs, defines the CTRL byte as follows for L_Data frames: FT 0 r 1 p1 p0 0 0 |
Beta Was this translation helpful? Give feedback.
-
|
|
Beta Was this translation helpful? Give feedback.
-
|
The screenshot you sent is not a raw TP1 (on-the-wire) telegram. It’s a cEMI L_Data.ind frame, and the circled Decoding the shown
So To verify, please share the full KNXnet/IP frame (Routing |
Beta Was this translation helpful? Give feedback.
Uh oh!
There was an error while loading. Please reload this page.
-
Hello
I am analyzing KNX TP1 telegrams and noticed that some frames start with the control byte 0xBE.
According to the KNX TP1 standard, the lower bits of the control field in a standard frame should be 00, so the most common value is 0xBC
Knx-Ultimate Version
4.1.24
Beta Was this translation helpful? Give feedback.
All reactions